D
daver
Just been asked to jump on a job which needs completing before end of Jan.
The guy I'm helping is 74 and very experienced.
We are doing 8 double bedded flats. 5 Complete and 3 to go.
17th Edition split boards with 5 Circuits
Kitchen Ring - 32A
Lights - 6A
Smoke - 6A
Then we have 2 radials in 2.5 - 1.5cpc. 1 to 2 bedrooms with 6 double sockets total. Then 1 to living room with 3 doubles.
Each is protected with 16A Type B.
I thought it should be 20A, but he gave no explanation as to the 16A.
The only factors I know about is that the cables pass through some insulation (2M) and then are clipped direct and quite short runs.
The question being. Is he correct with his choice????