D

daver

Just been asked to jump on a job which needs completing before end of Jan.
The guy I'm helping is 74 and very experienced.
We are doing 8 double bedded flats. 5 Complete and 3 to go.
17th Edition split boards with 5 Circuits
Kitchen Ring - 32A
Lights - 6A
Smoke - 6A

Then we have 2 radials in 2.5 - 1.5cpc. 1 to 2 bedrooms with 6 double sockets total. Then 1 to living room with 3 doubles.

Each is protected with 16A Type B.

I thought it should be 20A, but he gave no explanation as to the 16A.

The only factors I know about is that the cables pass through some insulation (2M) and then are clipped direct and quite short runs.

The question being. Is he correct with his choice????
 
It doesnt HAVE to be 20A however if you can up it from the 16 then it is fine on a 2.5 radial.

The cable is rated around 26A.
 
Last edited by a moderator:
depends on length of run, installation method and volt drop.
You could put the circuit on a 10 amp breaker if you wanted, probably not practical though. Get the guy to explain why he does things, it is the only way you wil learn..
 
there is no problem running any circuit on any size breaker as long as all requirements are taken into account, its just usally a 20a radial in 2.5 or 32 in 4mm etc....
 

Reply to Radial Circuit Protective Device in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top