Did you stop for breath there at all?
Ha ha I did but was pretty wound up when I got in from getting interrogated by the muppets that are doing this rubbish work ! Bit hard to explain while off the top of my head but it is garbage and as Pete has posted below to the OP on this older thread, surely by reading Appendice 15 even a layman or apprentice would understand basic ring finals and radials ! lol
 

  1. Reasons you shouldn't:
    1. It is prohibited by 434.2.1 - "The part of the conductor between the point of reduction of cross-sectional area or other change and the position of the protective device shall not exceed 3m in length..."
  2. 4mm clipped direct 36 amps . he is increasing not reducing the csa. Still a stupid idea thou lol.
 

  1. Reasons you shouldn't:
    1. It is prohibited by 434.2.1 - "The part of the conductor between the point of reduction of cross-sectional area or other change and the position of the protective device shall not exceed 3m in length..."
  2. 4mm clipped direct 36 amps . he is increasing not reducing the csa. Still a stupid idea thou lol.
Agreed Billy, although just had main contractor on phone texting asking me wtf is going on and why I'm not happy with it ? I said basically it's rough and bad practice and in extreme could overload one or more legs of essentially now a mixed circuit between ring and radial, also a pain for next electrician who comes into place and scratches his head plus ring system now flawed by the endless spur off spur carry on. He's telling me that a BS number isn't going to cut it with him etc.. I said I'll be the one doing the cutting in cutting ties with his gang ! lol
 
hi there, would like your views on this.. Jb off a ring main and run two or three socket,s on a 4mm radial. I myself don,t mind it. no current capacity issues.and no zs problem,s if rcd protected.Any thoughts.

Hi, there is no technical issue with this other than load distribution.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
radial from ring main
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
84

Advert

Thread statistics

Created
nick611,
Last reply from
Chr!s,
Replies
84
Views
23,437

Advert

Back
Top