I think the only thing you'll find on this is in the on-site guide, 8.2.4 - "In an A1 ring final circuit.....a non-fused spur should feed only one single or one twin socket outlet"
However, given that the point of the fuse in a fused spur is to protect the cable in the spur, and, subject to installation conditions, 4mm can handle more than 32A and will therefore be protected by the 32A breaker protecting the ring, I am struggling to find a problem with what you are suggesting nick611. As you say, it is not considered in BS7671.
Mind you, I have been at the port.....