Joined
Jan 13, 2022
Messages
6
Reaction score
4
Location
Falkirk
Hi. I will soon be wiring up my summer house. My plan is to run 10mm2 SWA from spare 50A breaker on my house consumer unit (approx 20m) to a 40A garage consumer unit with 6A MCB for 1.5mm2 lighting circuit and 32A for 2.5mm2 RFC. I plan to have 5 double sockets which will have heater, TV and console, Bluetooth speaker, phone chargers etc and the occasional lawnmower plugged in.
My question is are my plans ok or would I be better with a radial circuit?
 
One final point of note is to use decent glands for your SWA cable, and to have a flying lead for making sure it is properly bonded to the earth.

If affordable, I would use this sort of thing:

Yes, they are outdoor rated which probably you don't need, but do a really good job at clamping the cable. They also come with the "earthing nuts" that have a grub screw to lock them in place, and a tapped hole & screw for a ring terminal to add the flying earth lead. However, you can use the conventional ones with the "banjo" earth tag, or even just get the earthing nuts / piranha nuts separately.

However, double-check that is the right size for your cable!
 
One final point of note is to use decent glands for your SWA cable, and to have a flying lead for making sure it is properly bonded to the earth.

If affordable, I would use this sort of thing:

Yes, they are outdoor rated which probably you don't need, but do a really good job at clamping the cable. They also come with the "earthing nuts" that have a grub screw to lock them in place, and a tapped hole & screw for a ring terminal to add the flying earth lead. However, you can use the conventional ones with the "banjo" earth tag, or even just get the earthing nuts / piranha nuts separately.

However, double-check that is the right size for your cable!
Thanks again. Quality glands are one subject I am familiar with as I work in hazardous areas with Compex requirements. Appreciate the recommendation, i have mostly used Hawke but like the look of the earthing nuts you mentioned.
 

Reply to Radial or RFC for Summer house in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top