Hi I’m currently wiring my upstairs sockets on a 2.5 T&E protected by a 20A mcb do you think I will get nuisance trip due to the small size mcb or would you recommend making it a ring and using a 32A mcb. I don’t like rings so tried to stay away just I had some spare 2.5 but probably should have made it a 4mm radial
 
Your assessment of the likely load upstairs is going to be better than mine and a vital part of the design process, but I never have more than a couple of bedside luminaires (were 60W, now 10W LED) an alarm clock (4W) and a telly (32W) and DVD player (25W), so well under 1 amp for the lot...
And, of course, an RCD is needed for new work.
(However, mine has a rewireable fuse, no RCD, wooden floorboards and all the equipment listed above is class II and I'm in no hurry to change it.)
 
Last edited:
If you are doing a whole floor then a RFC makes more sense, unless you know for sure that the max load and length for VD limits (42m on 2.5mm) are met on the radial.

Probably a 20A radial is fine, it will cope with 2 * 2kW heater loads no problem, and I guess you won't have a 2kW induction motor up there on DOL starting!
 
Hi I’m currently wiring my upstairs sockets on a 2.5 T&E protected by a 20A mcb do you think I will get nuisance trip due to the small size mcb or would you recommend making it a ring and using a 32A mcb. I don’t like rings so tried to stay away just I had some spare 2.5 but probably should have made it a 4mm radial
It will be fine unless you're going to have tonnes of stuff plugged in and working all at the same time.

We're probably one of about 3 countries that uses rings. Everyone else uses radials and nobody struggles with tripping. Should be able to handle 12+ sockets comfortably.

It all depends on your design. If you're going to put 60 sockets in and know every room is gonna have DVD, XBOX, telly, PC, heaters, chargers, kettles etc on at all times then just do a ring or multiple radials. For normal use ie telly + dvd player in each room, charger here and there, the odd hairdryer or iron, it's fine.
 

Reply to Radial wiring help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
548
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top