Hi guys n gals.

I don't often do appliances but been looking at a range cooker of a regular customer (gas hobs, 3x electirc ovens).
It keeps blowing the 32A MCB with a flash at the back of the range (unable to position myself behind to see where from but suspect it's around the incoming connection).

I've tested all elements which weren't great on insulation test to earth but just about passed. They all had about 42ohm resistance through element.

I found a disintegrated light bulb which I removed and bypassed.
Although there was significant thermal residue on the light cables I couldn't see any bare conductor.

I've disconnected all connections at the main terminal of the oven and tested the terminals as there seemed to be liquid residue around it but that was ok.

I've checked all cables at the back for damage but found none and there is no thermal damage on the rear panels.

I got a insulation resistance reading of 9 Mohm between L & E for the whole oven.

I haven't dismantled the top of the oven yet to check the dials, switches, etc. as it was getting late.

Confusing me a bit how it's tripping the breaker even when none of the ovens are switched on.
Just wondering if anyone has any other suggestions what it might be?

Cheers in advance
 

Reply to Range cooker tripping breaker, even when all settings switched off in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

  • Question
A faulty element was my first thought of most likely culprit. however, if the big red cooker switch is turned off and the issue with the electrics...
Replies
1
Views
1K
Hi Brian, thank you so much for your reply. I read it at the time and thought I'd thanked you, so I'm sorry that i actually hadn't. I did have...
Replies
2
Views
3K
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
Replies
19
Views
3K
  • Question
It sounds like there is damage to the wiring underground. Do you know what kind of cable was used, in any underground wiring is used has to be UF...
Replies
3
Views
559
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
871

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top