Came across this problem at weekend brandnew range installed 40amp mcb on RCD side of split load board. Cooker isolator is 2 gang with socket out let. The rcd trips when ovens are on I know the reasons but was wandering how you go on with regs as all i could do was move mcb over to none rcd side of board so now you have a socket in a kitchen thats not got rcd protection do I

1. change cooker isolator to one gang without socket, don't think owner would be too happy as it would require backbox to be moved and some more tiling.

2. label socket outlet warning notice etc

3. Become a joiner!!!

Sounds like a faulty element, if all is ok when power is on the oven but nothing is switched on but soon as switch on the oven and the element heats ups the it is going to earth as insulation is breaking down thus causing element to trip RCD. When you test it later when cool it will seem as if the is no problem.

You will need to be there when oven is switched on and when it trips the RCD you will need to give it an insulation test straight away before it has time to cool down and fault dissappears.
 
i recon the prob could be a bad circuit on ur rcd which will work fine until u put a large load (like a cooker) on it and then it breaks down. try connecting the cooker to the rcbo for the shower tempororarily and see if this solves the problem
 

Reply to Range cooker tripping RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
523
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
952
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top