Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again
Would i be correct in saying the DNO will need to be notified and called out?
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again
Would i be correct in saying the DNO will need to be notified and called out?