Surely if you test at the CU you will get a perfect reading every time? Only if the rcd is functioning correctly , if its not then it wont pass the test no matter where you do the test.
If you test at the end of the circuit you will ensure a) the earth is continuous and the EFLI is low enough to operate the device in the required time. Eh ? this is a rcd test , what EFLI got to do with it ? that test is done seperately ?
Am not sure why you would want to ensure that the RCBO is fine, whilst the circuit and accessories that the device is meant to protect may harbour a fault that causes the (perfectly fine) RCBO not to operate in the required time? Then you have a problem with the wiring or accessories , not with the rcd , and you would need to investigate this seperately - your confusing what the test is for to be honest and the rcd is there to protect the user / occupier not the accessories.
I am not trying to be confrontational, I am simply confused as this is the first time I have encountered this method of recording trip times. I always record from the end of line.......