Just installing a new consumer unit for a customer. Split load board with 1 half RCD & the other half RCBO's. RCD & all but 1 RCBO has had good trip times, all sub 40ms at 1In & 5In, but the 6A RCBO for the kitchen lighting circuit is tripping at 40.8ms & 40.7ms at 5In. If I disconnect the outgoing live & retest the the trip times are 18.5 & 17.2. Anyone shed any light as to why this is happening & is it acceptable to test the RCBO without the outgoing ways connected?
 
As a path for current leakage, which would imbalance the coil. A high impedance on this path (or no path) would reduce ( or negate) the ability of the device to operate in the required time.

No?
 
Surely if you test at the CU you will get a perfect reading every time?

If you test at the end of the circuit you will ensure a) the earth is continuous and b)the EFLI is low enough to operate the device in the required time.

Am not sure why you would want to ensure that the RCBO is fine, whilst the circuit and accessories that the device is meant to protect may harbour a fault that causes the (perfectly fine) RCBO not to operate in the required time?

I am not trying to be confrontational, I am simply confused as this is the first time I have encountered this method of recording trip times. I always record from the end of line.......

I agree most of these regs are ambiguous,its good to question a lot of things as it shows we are thinking and not following like sheep but testing at the farthest point is not necessary.Quote from wiring matters Spring 2010 "Whether the RCD in question protects a number of circuits,eg on a split load board,or an RCBO is used to protect a single circuit,or an RCD is installed nearer the item of equipment being it is protecting,the tests can be carried out immediately on the load side of the device.Often it is suggested that an RCD protected circuit should be tested at the extremity,ie. at the same point at which the Zs measurement is taken.There is LITTLE TO BE GAINED in testing the RCD at the extremity of the circuit it is protecting.Firstly , the test is required to prove the RCD operates correctly.As the circuit in question will meet all other requirements ie earth loop impedance and volt drop,add little to the operating time of the device" Hope this helps.
 
^^^which is what i've been trying to explain for the last half hour lol.

Maybe, but not very clearly.

But thanks for that, it will definitely save me a lot of time in the future.

The only issue that remains is that of the OP. Why the difference in disconnection times with the the circuit connected or disconnected?

Any ideas?

As regards to ballasts etc "corrupting" the readings, if they are part of the circuit, they should conform to disconnection times.

Or am I wrong again?
 
FFS
I answered that in my first post.
Why do i bother.
[ElectriciansForums.net] RCBO 5In trip times.
 
FFS
I answered that in my first post.
Why do i bother.
View attachment 13794

Well not really. You said components of the circuit would "bugger up" the readings. I was under the impression the entire circuit should be tested, and conform.

Perhaps I am wrong and am willing to admit that. However, the NICEIC forms I fill in have a seperate box for the RCD disconnection times for every circuit. So when I fill these forms in, I measure the RCD connection times for each circuit, and record them appropriately.

Perhaps I should correct for ballasts and switches corrupting my results in the future. Do you have the correction factor for this as it will be very helpful?
 
I have to agree with biff on the above.

RCD test should be done with loads disconnected and a EFLI test prior to RCD testing.

As mentioned the times can be alot different if equipment is left connected.

GN 3 Rcd testing also makes mention of this.

Ok fair enough. I have pulled the GN3 off the shelf and it does say the load should be disconnected for the test. I was wrong on this point but my instinct still tells me the whole circuit should be tested. In the future i will test at the CU on a standard split load board and simply duplicate my results for the number of circuits that the RCD is protecting.

Sounds like a cowboy job to me, but if that is what is required then that is what I will do. Thanks to everyone who set me straight, as I was doing a lot of (apparantly) needless work.
 
We're only required to test the device, not the circuit for disconnection times of RCD/RCBO. I can see the reasoning behind testing the whole circuit but that is why we do R1+R2 tests to ensure we have continuity that will meet with disconnection times.

If you start taking into account ballasts & transformers where will it end?
 
It's just clicked, the test meter sends a 'pulse' to initiate the trip. Ballast/transformers/loads can absorb some of this 'pulse' and give spurious readings.

I think...
 
It's just clicked, the test meter sends a 'pulse' to initiate the trip. Ballast/transformers/loads can absorb some of this 'pulse' and give spurious readings.

I think...

Sounds reasonable. And I know I was (am still) wrong, But if they absorb leakage in a test situation, might they also absorb leakage in a genuine fault?
I am not trying to flog a dead horse but just think testing an RCD in 'laboratory conditions' defeats the point of the testing.
Anyhow, I concede defeat on this issue as the powers that be have ruled otherwise.
Saves me a lot of time :)
 
Consider putting a nail through a cable, the fault will be greater than 30mA.
 
However, the NICEIC forms I fill in have a seperate box for the RCD disconnection times for every circuit. So when I fill these forms in, I measure the RCD connection times for each circuit, and record them appropriately
Whilst each line has provision for RCD times you only have to record the times on the line the RCD itself is on, unless you're saying that you don't actually have RCD's on their own line?
 

Reply to RCBO 5In trip times. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top