HI guys got this of another website what do you make of it



Do we need a C or D rating on a RCBO?

Not as daft as it my first seem. The magnetic part of the MCB ensures the MCB will trip in the required time in the event of a short circuit.

With the RCD being used any short circuit to earth with trip the device using the RCD part of the device.

So the B rating will only be required to ensure the device will trip if you get a short circuit line to neutral.

If one considerers a ring main of 106 meters of 2.5mm twin and earth (Max allowed for volt drop) fed from a TN-C-S supply so we can assume the incomer impedance line to neutral is 0.35Ω to trip a B32 trip will need 5 x 32 = 160 Amps so 230/160 = 1.4375Ω minus 0.35Ω that’s 1.0875Ω the twin and earth is doubled up so that’s 0.009Ω per meter which will mean it will trip at up to 241.6 meters.

So a B type RCBO will trip on the magnetic part of the device. But re-calculate that using a C type device and we drop to 81.94 meters and for a D type device 2.083 meters.

The original Dorman/Smith type LoadMaster MCB did not have any magnetic part and was a plain 5 to 70 amp MCB then we had the 1 to 4 type which was replaced with B to D type.

The maximum disconnections times given in the 17th Edition is for earth faults not line to neutral faults and any thermal trip will open before we get cable damage.

If we still need to consider the magnet tripping part of the trip will this place any limits on wiring which at the moment we are failing to consider


 
The other guy has the wrong end of the stick. cable lengths and resistances are required to be measured such that short circuits and earth faults do trip the relevant device. That is why we need to measure and check EFL resistance on all circuits.

The relevance of B, C and D are the start up current vv the standing current. I have just installed 8 HF lighting units with a standing current of ~5 Amps and placed it on a 6A MCB. With a B type the MCB tripped on switch on. With a C type its fine. The RCB part of the RCBO has no relevance to this consideration.
 

Reply to RCBO B,C or D rating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
    • Like
2
Replies
22
Views
2K
  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top