RCBOs consume between 1.5 and 2.5 watts for each pole - according to Wylex. Have a CU with largish bank of DP RCBOs then the annual cost of just having RCBOs is substantial. It is not just a few quid a year in electricity costs to have them. My question is:

Do RCBOs still consume electricity when switched off?
 
Last edited:
Unless they have changed the design, the Wylex ones are not completely off when open. I remember IR testing the busbar of my own board and found they have a hundred or kOhm still. However, I don't know if that is the main powering sources or not (i.e. if switching on changes it).

The Harger RCCB I have tried seem to IR open on both sides, so I guess they use a capacitive divider. That should be more energy-efficient than just a resistive divider but I don't have a spare Wylex RCBO to test those theories out.
 
I've only skim read this thread, but it looks as though this video might be relevant:
(they also measure some RCBOs, neons, and USB sockets from memory)

 
I always try to fit MCB/RCBO/fuses as low a value as possible, to give added protection in fault conditions on connected appliances.
But at #49 you say "Which brings me to the point of using the highest mcb rating you can to reduce the bi-metal strip bending consuming energy and getting warm"

In Other posts, you complain about loss, but you say you use the smallest cable you can get away with.

Small/Large Thick/thin which is it because you seem very confused.
 
But at #49 you say "Which brings me to the point of using the highest mcb rating you can to reduce the bi-metal strip bending consuming energy and getting warm"

In Other posts, you complain about loss, but you say you use the smallest cable you can get away with.

Small/Large Thick/thin which is it because you seem very confused.
Given chance he would argue with himself and I'm sure he did in a thread a little while ago
 
That Efixx video was useful, even at double the originally measured cost it seems the RCBO is only using around £1/year so less than depreciation if you assume a 10 year period for them and as-new cost of around £20 (and given the cost of AFDD well below their depreciation cost).

What was also said at the end of the video was about much higher usage on "stand by" like the speaker with Alexa, managing to simultaneously steal your money and privacy!

From memory by VM router/modem takes about 6W so is more like £20 per year and way more than my CU.
 
But at #49 you say "Which brings me to the point of using the highest mcb rating you can to reduce the bi-metal strip bending consuming energy and getting warm"

In Other posts, you complain about loss, but you say you use the smallest cable you can get away with.

Small/Large Thick/thin which is it because you seem very confused.
You have poor comprehension. Read what I wrote again. It was clear enough.
 
I've only skim read this thread, but it looks as though this video might be relevant:
(they also measure some RCBOs, neons, and USB sockets from memory)

Excellent vid. Even Big Clive commented in comments section. They pointed to another vid at Lewden testing AFDDs. AFDDs combine four fault protectors in one unit. The longevity of AFDDs maybe in question they have complex electric boards inside, unles you pay a fortune for the top quality makes. But you can get around the AFDD regs by installing a ring final circuits supplying sockets, with 4mm cable and a 40A RCBO/MCB.
 
Last edited:
  • Funny
Reactions: DPG
[ElectriciansForums.net] RCBO energy consumption
 
But you can get around the AFDD regs by installing a ring final circuits supplying sockets, with 4mm cable and a 40A RCBO/MCB.
Additionally, a ring final circuit is defined in t'regs as having a 30 or 32 amp protective device:

433.1.204
Accessories to BS1363 may be supplied through a ring final circuit, with or without unfused spurs protected by a 30A or 32A protective device complying with BS88 / BS3036/ BS EN 60898 / BS EN 61009 etc.

If we went back to 14th edition things were a bit different then.
 
Last edited:
That Efixx video was useful, even at double the originally measured cost it seems the RCBO is only using around £1/year so less than depreciation if you assume a 10 year period for them and as-new cost of around £20 (and given the cost of AFDD well below their depreciation cost).

What was also said at the end of the video was about much higher usage on "stand by" like the speaker with Alexa, managing to simultaneously steal your money and privacy!

From memory by VM router/modem takes about 6W so is more like £20 per year and way more than my CU.
52p per ann. to run a neon light, which will be approaching a £1 now energy has risen. Have three and £3 per ann. With all the rest of the standing losses in the hosue and in the CU you can pay for a night out. Add all this up over a whole nation and maybe a fossil fuel power station feeds it.
 
52p per ann. to run a neon light, which will be approaching a £1 now energy has risen. Have three and £3 per ann. With all the rest of the standing losses in the house and in the CU you can pay for a night out.
Either you have a massive CU full of circuits, or you live somewhere incredibly cheap!

Even up here in Dundee, which is hardly known for affluence, I won't get much of a night out on the £5 of my flat's always-on RCBOs.
 
Status
Not open for further replies.

Reply to RCBO energy consumption in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3 4 5
Replies
65
Views
6K
I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
352

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top