Done a board change at domestic property ti an rcbo and spd board, previously had old rewireable fuse board, and done all my ir tests and so on and everything seemed good, lo and behold I get a phone call that the downstairs sockets have tripped, I told them to remove all loads and the circuit still tripped overnight.
I then went back to job and found a loose neutral in one of the sockets which I then connected and everything was back up and running, keep in mind that security system is on this circuit via a unswitched spur.
I then decided to redo an ir test only to find that there was a complete dead short between all conductors even after removing all loads and fuse from the spur and also removing the wires from the rcbo and earth bar.
Any help would be greatly appreciated.
 

Reply to Rcbo intermittently tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
448
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top