Have a problem with a Wylex 32A Type C RCBO that has tripped to a utility room and heating plant room to a west London mid terraced house.
It will not reset even with all loads removed. I tried swapping the line and neutral conductors to an adjacent same rated RCBO and the same happened. I tested the ring between L-N at the utility sockets and incoming spur to the plant room and was 0.42 ohms. I only had time for a quick look on xmas eve and will return on Monday to carry out further tests. But not having had many issues with RCBO's I need some advice on how to test these devices properly and what the possible causes could be. There is no history on this fault as the property is vacant and the problem miraculously appeared!

Cheers
 
Very good point brought by Davesparks.... if we have 230v RMS then peak voltage is around 320v so exactly what would an insulation test that isn't in excess of this proof because it may not show any issues or failed readings where a 500v would unless its very poor value.
 
Always use 500V for circuits operating at 240V AC, there's no point testing insulation resistance at a voltage less than the peak voltage of the supply.

On a new install / additions then definitely 500V. Not faulting on an existing installation unless you are absolutely 100% that all loads are disconnected and after 250V has shown clear. Like I said very rare I would use 500v outside new installation. To be honest, in this scenario 500V will provide no benefit over 250V and only the risk of damaging equipment which will give the OP another problem to deal with.
 
Very good point brought by Davesparks.... if we have 230v RMS then peak voltage is around 320v so exactly what would an insulation test that isn't in excess of this proof because it may not show any issues or failed readings where a 500v would unless its very poor value.
You have answered your own question there, the fault is present at 230v and is operating the RCBO, therefore higher than that is not required to trace the fault. I appreciate what 500VDC testing provides, but in the case of locating a fault that is tripping a 30ma RCD, 250VDC is adequate and with no risk.
 
Last edited:
...Right! i have finally got it...the 0.42 is the duration our poor OP lasted,from original post,1.00 being a full day of 24 hours,corrected for temperature...:icon12:
Sigh.
Peg, he's already said what the measurement was all about mate. It was a completely pointless exercise as far as fault finding is concerned but never mind.
Actually, thinking about it maybe you've got more of a point.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
RCBO not restting
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
77
Unsolved
--

Advert

Thread statistics

Created
sparkside1,
Last reply from
Geordie Spark,
Replies
77
Views
18,936

Advert

Back
Top