sparkside1

Hi all

Have a problem with a Wylex 32A Type C RCBO that has tripped to a utility room and heating plant room to a west London mid terraced house.
It will not reset even with all loads removed. I tried swapping the line and neutral conductors to an adjacent same rated RCBO and the same happened. I tested the ring between L-N at the utility sockets and incoming spur to the plant room and was 0.42 ohms. I only had time for a quick look on xmas eve and will return on Monday to carry out further tests. But not having had many issues with RCBO's I need some advice on how to test these devices properly and what the possible causes could be. There is no history on this fault as the property is vacant and the problem miraculously appeared!

Cheers
 
Very good point brought by Davesparks.... if we have 230v RMS then peak voltage is around 320v so exactly what would an insulation test that isn't in excess of this proof because it may not show any issues or failed readings where a 500v would unless its very poor value.
 
Always use 500V for circuits operating at 240V AC, there's no point testing insulation resistance at a voltage less than the peak voltage of the supply.

On a new install / additions then definitely 500V. Not faulting on an existing installation unless you are absolutely 100% that all loads are disconnected and after 250V has shown clear. Like I said very rare I would use 500v outside new installation. To be honest, in this scenario 500V will provide no benefit over 250V and only the risk of damaging equipment which will give the OP another problem to deal with.
 
Very good point brought by Davesparks.... if we have 230v RMS then peak voltage is around 320v so exactly what would an insulation test that isn't in excess of this proof because it may not show any issues or failed readings where a 500v would unless its very poor value.
You have answered your own question there, the fault is present at 230v and is operating the RCBO, therefore higher than that is not required to trace the fault. I appreciate what 500VDC testing provides, but in the case of locating a fault that is tripping a 30ma RCD, 250VDC is adequate and with no risk.
 
Last edited:
...Right! i have finally got it...the 0.42 is the duration our poor OP lasted,from original post,1.00 being a full day of 24 hours,corrected for temperature...:icon12:
 
...Right! i have finally got it...the 0.42 is the duration our poor OP lasted,from original post,1.00 being a full day of 24 hours,corrected for temperature...:icon12:
Sigh.
Peg, he's already said what the measurement was all about mate. It was a completely pointless exercise as far as fault finding is concerned but never mind.
Actually, thinking about it maybe you've got more of a point.
 

Reply to RCBO not restting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top