rcbo on ring circuit | on ElectriciansForums

Discuss rcbo on ring circuit in the Australia area at ElectriciansForums.net

C

coxy84

iv got a 32 type b rcbo covering a socket ring circuit with 12 points on it. its a tns system.
it on a run of about 45metres

my problem is i cant seem to get it trip within the acceptable time.

1x 198ms 5x way above 40ms

iv replace it with another unit thinking the rcbo was faulty but im getting pretty much the same results.

any idea's?
 
If there were loads on when you tested that'll almost cerytainly be the reason....anything with a capacitor..(fridge...fluorescent light etc) will hold a charge when the power is interrupted,your meter is fooled into giving a higher trip time.....Disconnect all loads and it'll be ok.
 
If there were loads on when you tested that'll almost cerytainly be the reason....anything with a capacitor..(fridge...fluorescent light etc) will hold a charge when the power is interrupted,your meter is fooled into giving a higher trip time.....Disconnect all loads and it'll be ok.

cheers!
there might have been a fridge pluged in i will check tommorrow!
 
I had the same results with my Fluke 1652 on a smoke detector circuit, but no loads were on the circuit, just the base plates and the wiring. Used a different tester and got same results, so changed RCBO and got the same results again.

x1 310
x5 50m/s

Disconnected wiring at board, tightened screws on load outlets and re tested. Times were OK. Reconnected wiring, and hey presto, the same bad results as above. Checked wiring, only 2 detectors on circuit, all OK.

I have no idea what to do next!

Did not see any magic wands in the wholesaler! Going to change batteries in tester and see what happens.

Gonk43
 
Trying to get my head round this but no matter what load is on the cct its the RCBO tripping time thats being tested ,if ramp tested yes the leakage would bring it down the mA reading so I would go with faulty RCBOS or something stupid like a damaged earth fly lead.

Try connecting the RCBO to another cct and do a series of tests not just a couple and see if there are any big variations with the results.

If when loads are connected to the cct and the tripping time does not come within the regs then its got to be a fail as its not doing the job its their for IMO.
 
I usually test rcd's & rcbo's at the board, remove the live conductor from the rcbo, connect to live terminal at the rcbo & test, it guarantees no load when testing, Test rcd's the same way switch off all but 1 mcb then test sdame way as rcbo. I use a megger 1552 as it will do 2 lead RCD testing.
 
Trying to get my head round this but no matter what load is on the cct its the RCBO tripping time thats being tested ,if ramp tested yes the leakage would bring it down the mA reading so I would go with faulty RCBOS or something stupid like a damaged earth fly lead.

Try connecting the RCBO to another cct and do a series of tests not just a couple and see if there are any big variations with the results.

If when loads are connected to the cct and the tripping time does not come within the regs then its got to be a fail as its not doing the job its their for IMO.


Not the case,although I can see where you are coming from.....a load is likely to increase the tripping time,so the RCd has to be tested with no load. The usual reason is a load with a capacitor,this holds a charge for a split second after the tester trips the RCD,the tester may pick up this charge and be fooled into giving a higher trip time. On my tester you can actually see the display figures rolling for a fraction of a second after you've heard the click of the rcd tripping.
 

Reply to rcbo on ring circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
980

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top