Discuss RCBO on TT earthing is it safe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes, that’s right.Thank you for your kind reply.
Sorry I meant because the rcbos are single pole it wouldn't disconnect the neutral due to a earth to neutral fault. It would detect it however and disconnect the phase only. Am I right? And a double pole isolation is good enough no need for an rcd?
You are of course right Spin, but I couldn't resist with the above.Yes, that’s right.
No offence to you either chap, just having a giggle over a late lunchIs it safe to use single pole RCBOs on a TT earthing system without an rcd and just a double pole breaker?
What would the max allowable earth resistance be to cut out a earth to neutral fault?
Double check manufacturers instructions if using RCBOs on a TT system as some state that certain types are not suitable for use such as Schneider single pole devices.
You do need a method of isolating all live conductors on a TT system but this can be done at source by one single pole device, however I personally would install double pole devices on TT systems on all final circuits as there could be quite a large potential difference between neutral and earth and a double pole device would allow you to safely isolate both live conductors on a final circuit.
Yes.Hi everyone,
I would like to rob a bank, as long as I don't hurt anyone would that be ok?
If just one of you random strangers says 'yes' then I believe that would suffice for me to go ahead.
Many thanks.
This problem is present with SP RCBOs regardless of which earthing system is in use.
The RCBO will detect the fault on the N and disconnect the L.
NoYes.
Because they're the manufacturers and they can say that.All good.
Why do some manufacturers specifically say do not use on TT systems?
Reply to RCBO on TT earthing is it safe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net