rcbo only resets when other mcb is off | Page 3 | on ElectriciansForums

Discuss rcbo only resets when other mcb is off in the UK Electrical Forum area at ElectriciansForums.net

Joined
Apr 7, 2012
Messages
63
Reaction score
2
Hi there, i have recently wired a lighting circuit and a radial circuit for two socket outlets. Run the feeds for both circuits using a 5 core 2.5mm high tough cable from the distribution board to a jointbox. From the j/b i took my feed for lights and feed for sockets, used same earth for both circuits. Lighting circuit is on a 10a mcb and radial for sockets is on a 20a rcbo.
Completed wiring everything worked fine until i hit test button on rcbo and found it would not reset. Only when i switched off the 10a mcb for lighting circuit would the rcbo reset, found this very strange! Have tried different rcbo, but same thing happens, checked all wiring everything looks ok. I know using the same earth for both circuits is not ideal but can't see how it could effect the test button. Really not sure about this one any advice would be welcome.
 
Both mcb and rcbo are fitted in a 3 phase d/b which is protected by a 300ma s type 3 phase rcd, so neutrals are not independent. How could this be effecting rcbo through test switch?
 
This may leave a lot of TT systems a bit hazardous, and there is a lot of TT systems about!!
it sounds like the whole contracting world has had arguments with nic engineers about ee values!!

Well at least the Nic's recommended 100 ohm Ra is a 100 ohm lower than what is recommended in BS7671!! lol!! Both are basically useless in real terms, and both totally relying on a single RCD as the main protection against earth faults...
 
Could well be capacitance between the cores. The leakage at 50Hz will be slight, but it just might be enough to cause difficulties when resetting the RCD.

Being capacitive leakage, it won't show on an insulation test unless your tester can do AC. Most are DC only.
 
Over a distance of 5 metres, are you being serious?

Have a look on Google for cable capacitance, we’re talking a short distance not half way across the Gobi desert.
 
Last edited by a moderator:

Reply to rcbo only resets when other mcb is off in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

Indeed, that was my thought, a B20 having a 60A instantanious trip should easily cover a inrush for a domestic fridge, and if the fridge and...
Replies
11
Views
541
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
485

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top