brucey2343

Hi,

My QS believes an RCBO provides fault protection only, and we have to enter N/A on the test certs for the additional protection. Is this correct? We deal with TN-C-S and TN-S domestic. I assumed it provided both

Thanks!
 
If it's a 30mA trip current then no, it is most definitely incorrect.

It provides fault protection via the MCB and additional protection via the RCD element, and of course earth fault protection where you are unable to achieve a sufficiently good Zs (typically TT systems).
 
So a 30ma RCBO does provide fault and additional protection? Is there somewhere this is in writing?
 
I am referring to the schedule of inspections, 4.19 "RCD(s) provided for additional protection/requirements - includes RCBOs (411.3.3; 415.1). 411.3.3 states additional protection must be provided for sockets not exceeding 32A and mobile equipment for outdoors not exceeding 32A (I assume this to be plug-in lawnmowers etc). So I am correct, 30mA RCBOs are both ticks on 4.18 and 4.19 of the inspections?
 
Yes if it has tripped within the required times.
 
And what he believes an RCBO is.

And if he says combined MCB and RCD, then ask him why it doesn't provide additional protection is it has a 30mA trip current. Will be very interesting to hear his reasoning.
 
It's a bit scary isn't it?

I agree,but i would have gone for Quite Scary (QS:rolleyes:)

Forgive me...it's blowing a gale out there,and i should be sticking a scaffold tower up,so,i'm feeling buoyant;)
 
Hi,

My QS believes an RCBO provides fault protection only, and we have to enter N/A on the test certs for the additional protection. Is this correct? We deal with TN-C-S and TN-S domestic. I assumed it provided both

Thanks!
QS needs re educating
 
It depends on what the purpose of the RCD is for. If it is for a high Zs then it is for fault protection but only if additional protection is not required. If it is for high Zs and for example sockets then it is still for both fault and additional protection.
 

Reply to RCBO protection type, to settle a debate in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
558
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
925

Similar threads

  • Question
Hi All, Looking for some advice into my build. What I've basically done is add additional RCD protection to my 100% off-grid 12V 3300W Inverter...
Replies
0
Views
176
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top