First thought
Residual current devices, rated at 30mA, in order to comply with regulations must trip at between more than 50% of rated current and rated current (i.e. 16mA to 30mA).
With two residual current devices in series RCCB then RCBO the actual tripping current of the RCCB was less than that of the RCBO effectively giving negative earth fault discrimination.
With one final ring circuit for the whole house the total earth leakage then occasionally exceeded the tripping currect of the RCCB but not the RCBO. (washing machine, kettle, iron etc all on at once)
Am I close?
Ok shakin stevens, I reckon the neutrals of that ring circuit were connected into the rcbo, the rcbo neutral connected to the neutral bar like normal. but to keep that circuit in balance, volts, you took a fly lead from the rcbo to the rccb so that the phase and neutral would be of equal voltage within the rccb?
Shakin, I really do mean the '?'
sparkz,
if there was a fault that tripped the RCD, then obviously all the circuits protected by that RCD would cease to be live. If you add an RCBO on a different phase bar within the same consumer unit, that circuit fed from that RCBO would not be affected and thus stay live whilst the rest of the installation would have been cut off by the RCD. The obvious benefit in this case would then be that upstairs lights would still be operational as well as the fire alarm system when there is a fault on the RCD side.
It could just be a company policy that upstairs lights and fire alarm systems are protected seperatley?
Thank you everyone....appreciate all your help especially "simonatlondon" o you a drink falla . Which reg's does this come under? so i can have a read.
Gonna take a wild stab in the dark here. We have an RCCB feeding an RCBO. The RCCB as a device has no connection to earth, where as an RCBO does through that little white wire.(am I getting warmer?) I actually dont know why this is, I always thought that an RCBO was an MCB and RCD all in one. Neither an RCD or MCB has an earth wire, so why does an RCBO ? There must be a reason. Whetever that reason, this is what the problem is. If I am wrong, I am open to being shot down in flames, but its all I can think of at the moment !
Just had another thought.........................................................................Er, no thats not it either !
It may have only taken two minutes to fix, but how long did it take you to suss out Shake ?