I'm stuck here fellas.

I have a radial with only one double socket outlet in 2.5mm T&E on a 20A RCBO running five meters in surface mounted trunking. TN-S, R1 and R2 good, 243V measured, Ze 0.12, Zdb 0.29, Zs 0.36, IR all +200MOhms.

RCD trip tests all ok at 0 and 180 and ramp 24mA.

Now these sockets are only used for one thing, two 580W water distillers.

Both have been clamped during operation and are drawing 2.4-2.6A as expected.

Both have been IR tested L-E & N-E and +200MOhms.

I am stumped to the point where I may run in a new socket on a new RCBO, cost not an issue the customer just wants it stopped.

My concern is the issue could be with one or both the distillers units and not the circuit.

I don't have a low current clamp meter so cannot measure earth leakage directly.

Any ideas where to look next, I'm still on the job by the way.
 
Is it one of the appliances, or both?
Is it conceivable to run another dedicated circuit, RCBO controlled and see which of the 2 are causing the problem.

It could be as simple as the socket being faulty
 
Is it one of the appliances, or both?
Is it conceivable to run another dedicated circuit, RCBO controlled and see which of the 2 are causing the problem.

It could be as simple as the socket being faulty
There are already three circuits there, the new dedicated circuit, the old ring main and a random MIC metal clad single.

All three circuits have tripped but they "manage" it by keeping them on the recently installed dedicated circuit.

They are not the most helpful, like I said will try the manufacturers and look to FCU them.
 
Asked on the forget information you have given I would say that the equipment is faulty, elements may appear to be fine and test ok but as soon as they get hot the resistance to earth diminishes..
The fault current might even be high enough to take out an mcb
 

Reply to RCBO socket circuit tripping. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
978
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top