Can you help with a problem we had today.
We have installed a ring circuit of exterior 70 watt MHi floodlights around the perimeter wall of a building. There are 16 lights on a ring of fire tough 2.5 R1 + RN with 1.5 R2.
The cable length is 230 meters. The ZS = 0.71. R1 = 1.59. RN = 1.59. R2 = 0.95.
We installed a 16 amp 10K RCBO but the reading we got on RCD test were X1 550/550 X5 440/ 440.
Both reading outside of Bs7671.
These reading were obtained with a raw circuit, straight out of the RCBO into the ring.
Does anyone have an idea why the readings were so high so as not to comply?
We have as a temporary measure (we hope) installed a MCB with no problems.
Regards
Gadget.