why dont u tst at the DB on socket circuits?, know its easy to go to a socket but it is quicker to just do it at the DB
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss RCBO Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
sorry to jump on this thread, but is this thread saying that it is ok to test rcbos at the DB rather then at the end of line, is this same in domestic and industrial i thought we had to go do it at end of line
Exactly the same way as you'd test an RCD: 0.5Idn (no trip within 2 sec), Idn 0deg, Idn 180deg, 5Idn 0deg, 5idn 180deg.
As mentioned, you may need a long, thin probe to make a connection to the Neutral out terminal of the RCBO, as they are recessed by 25-30mm or so on most types.
Also, you need to disconnect the outgoing circuit when performing insulation resistance tests on it. The disconnection is only single pole so the Neutral will go straight through to the busbar.
You should disconnect the Neutral flying lead when testing on the busbar side of the RCBO
Many have a functional earth connection, so this should be disconnected for IR testing too (manufacturer's instructions).
Simon.