why dont u tst at the DB on socket circuits?, know its easy to go to a socket but it is quicker to just do it at the DB
 
so do u , put the probes on the load side of rcbo, and just put a crock on the earth bar (with all other earths and bonding at it )
 
sorry to jump on this thread, but is this thread saying that it is ok to test rcbos at the DB rather then at the end of line, is this same in domestic and industrial i thought we had to go do it at end of line


It is the ONLY place to test RCD's when conducting proving tests, check with any of the manufacturers and you will be told the same thing!! No problem testing that RCD's are working from remote socket outlets etc, but when conducting time and current trip functions, these should always be conducted at the terminals of the RCD device itself!!

Yes there is one or maybe 2 manufacturers that suggest or prefer short bits of wire be connected to the RCD and tested conducted from the ends of those short wires...
 
Had a similar problem with hager rcbo's once and after a call to there technical dept. Was told the reason they do not trip with load connected is well known because of capacitance in the circuit.
 
Exactly the same way as you'd test an RCD: 0.5Idn (no trip within 2 sec), Idn 0deg, Idn 180deg, 5Idn 0deg, 5idn 180deg.
As mentioned, you may need a long, thin probe to make a connection to the Neutral out terminal of the RCBO, as they are recessed by 25-30mm or so on most types.

Also, you need to disconnect the outgoing circuit when performing insulation resistance tests on it. The disconnection is only single pole so the Neutral will go straight through to the busbar.
You should disconnect the Neutral flying lead when testing on the busbar side of the RCBO
Many have a functional earth connection, so this should be disconnected for IR testing too (manufacturer's instructions).

Simon.


Many thanks for the info don't think i replyed before but i bet that one don't come up in the February exam as a re take from October.

Thanks again..Ian.
 

Reply to RCBO Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
300
  • Question
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
    • Like
2
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top