What sort of test equipment have you got, My advice if you have one of the latest 17th testers would be to temp conect a 13a SSO to a suitable point of the lighting circuit and do the test as you would on a SSO circuit Simples

Strange that, seeing as virtually all the manufactures all state testing at the RCD units terminals!! Nothing wrong with testing down stream, but not for any official/recorded testing!! As has been already stated your testing the RCD unit, not the circuit it's connected as well!!

Are you sure your not getting confused with ELI testing.... lol!!
 
Strange that, seeing as virtually all the manufactures all state testing at the RCD units terminals!! Nothing wrong with testing down stream, but not for any official/recorded testing!! As has been already stated your testing the RCD unit, not the circuit it's connected as well!!

Are you sure your not getting confused with ELI testing.... lol!!

Exactly-the reason for testing at the terminals of the device is that any capacitance in the circuit (ballasts etc.) while not affecting the actual disconnection time, affect the displayed disconnection time on the test instrument.
 

Reply to rcbo testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
605
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
773
davesparks
D
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top