Timotei
-
Call out for tripped 20A RCBO on TT system, 3 Halolite T4 fluorescent cabinet lights (class 2) on 3A FCU from radial socket circuit, trips occasionally when lights are switched on.
Circuit tested including IR, all results good, RCBO tested including ramp test, all good.
Connections checked, all good.
No unexpected earth leakage shown with clamp meter on tails.
Can recreate the trip when all 3 lights are on, but turning any one off at its own switch so that only 2 are switched on / off via lightswitch the fault cannot be recreated.
Thoughts please.
Circuit tested including IR, all results good, RCBO tested including ramp test, all good.
Connections checked, all good.
No unexpected earth leakage shown with clamp meter on tails.
Can recreate the trip when all 3 lights are on, but turning any one off at its own switch so that only 2 are switched on / off via lightswitch the fault cannot be recreated.
Thoughts please.