Susie
Rcds operate when there is imbalance of the Live and neutral (current flowing to earth through a fault may cause this imbalance
0.03 is the milli amp rating of the rcd for the earth leakage that will cause it to operate.
Any other rcd in series with this 30 milli amp rcd will also operate under a fault condition
There are rcds that permit a time lag that overcomes this issue, they are called time delay rcds and generally a 100 milli amp rcd, time delayed, will be used on the supply sid,e whereas the 30 milli amp will be used on the loaded side
You appear to have two 30 milli amp rcds in series and a fault in the garage is causing operation of both
Des that was really well explained, and a piece falling into the jigsaw, I think I might get it now- thank you!