Hi,
I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted.
The issue i have is that when i connect one of the three lighting circuits it trips the other two lighting circuits together with one of the 32amp ring circuits!!!
I thought borrowed neutrals at first, but why would the 32amp ring circuit trip at the same time???
 
A bonded pipe touching the foil?
The cause was someone putting a screw into the stud wall going through the tin foil insulation and catching the tail of phase one, the tin foil insulation must be getting earth through some of the screws that various Dbs are screwed in.

The location is basically a pump house wooden shed that has had insulation and ply skin.
 
Last edited:
The cause was someone putting a screw into the stud wall going through the tin foil insulation and catching the tail of phase one, the tin foil insulation must be getting earth through some of the screws that various Dbs are screwed in.
Well that's a nice case study .... tails behind insulation in a stud wall.
It sounds like someone could have once done a bit better!
 
Well that's a nice case study .... tails behind insulation in a stud wall.
It sounds like someone could have once done a bit better!
I’ve altered it since and run both phases + N in surface mounted in some trunking.

Bit untidy looking but a bit safer
 

Attachments

  • [ElectriciansForums.net] RCBO tripping issues
    IMG_1898.jpeg
    119.8 KB · Views: 46

Reply to RCBO tripping issues in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
376
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top