S

sparkygrant

Hi all help please,I tested a6 amp rcbo30ma at board with out load connected the rcd results are 310ms at times 1 and 50ms at times5 so I changed it thinking it was faulty tested new 1I fitted got same results I then rcd tested another rcbo in the board another lighting circuit results are fine I then tuck the 1I tuck out because I thought it was faulty and put in my board at home and the results was fine has any one come across this before and can someone please help with this situation cheers
 
If there is some electrical equipment present that has a capacatative value that is connected across neutral to earth as may the case in some electronics, particularly on lighting then this can absorb some of the current generated by the tester and delay the switching of the RCBO.
Then again a very long length of cable can also have this effect but not normally at these levels.
You could try disconnecting the outgoing neutral or earth and seeing if that has an effect.
Try and get the RCBO as isolated as possible from all other influences.
 

Reply to rcbo tripping times in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
385
  • Question
well then, must be a fault on the circuit, a faulty appliance if a power circuit or a faulty RCBO.
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top