I came across something new today. When I removed the main earth to do ze the rcbo tripped. Put the earth back in and it's fine. Can anyone explain what is going on?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Rcbo tripping in the UK Electrical Forum area at ElectriciansForums.net
Just to add a little to @SparkyChickWithout being there and being able to test and inspect, I can't say why it happened, but what I can say is you most definitely should not be removing the main earth with the power on.
So you are disconnecting the main earth whilst the board is still energised and circuits are switched on?I came across something new today. When I removed the main earth to do ze the rcbo tripped. Put the earth back in and it's fine. Can anyone explain what is going on?
one life. live it. where's the fun in safe?So you are disconnecting the main earth whilst the board is still energised and circuits are switched on?
Unbelievable!
Very true, I had made the assumption it was still energised. There might have been something else allowing the RCBO to trip even though the main power was isolated, though in itself that is worrying!nowhere in the original post did it say that the main isolator was still energised.
both myself and others have in our own minds assumed that it is energised because the fault described would in most circumstances require the power to be on for it to manifest itself.
@Vortigern has made a very valid point
nowhere in the original post did it say that the main isolator was still energised.
both myself and others have in our own minds assumed that it is energised because the fault described would in most circumstances require the power to be on for it to manifest itself.
@Sonia Norman
if indeed you are testing Ze with the main isolator switched on, I hope you have learnt something from the posts.
if in fact the main isolator was off then there is something unusual going on there, possibly to do with a current flow between N and earth via the rcbo fly lead .
@ everyone else, remember that we are all human and don’t get everything right all the time.
I am sure if we look back at our own mistakes and failures, the odd one will make us cringe.
I for one can look back at a couple of events that didn’t go horribly wrong, more due to good fortune than perfect methodical working practices.