Hi There just had to go and do a quick check on a suspected RCBO tripping.
Tested the RCBO and am satisfied it is ok and working fine, customer is complaining that only the wall lights in the lounge keep blowing lamps and trip keeps going but it is only the wall lights none of the other lights on the circuit.
SO not wanting to get to involved straight off as not getting paid at this point.
I done a insulation resistance test live/neutral together and to earth 13.40M ohms
With all lamps in place sitches closed etc. so trying to explain that this is technically satisfactory. any way they are also saying that it trips of its own accord with nothing turned on. SO i went to the switch plate Feed and neutral are at the switch so from the switch i seperated the circuits and tested out to the centre light (switch wire and neutral then both to earth with lamps removed is between 11 and 13 M ohms) done the same to the wall lights (with lamps removed and just switch wire, neutral and to earth all seperate) same figure. so then tested the neutral and earth of the out going feed to the rest of the small extension same figuer and they have the same style lights fitted throughout. Could this be cheap light fittings?? any advice would be welcome.
I did also explain that using cheap lamps is also a common problem as they dont last but they argued back with that its on the wall lights that do it in that room none of the others go?
I have not gone to far into it as Im am getting over the back operation and shouldnt be working anyway and it was a free test just to try and establish if it was something simple or not.
Thanks
Tested the RCBO and am satisfied it is ok and working fine, customer is complaining that only the wall lights in the lounge keep blowing lamps and trip keeps going but it is only the wall lights none of the other lights on the circuit.
SO not wanting to get to involved straight off as not getting paid at this point.
I done a insulation resistance test live/neutral together and to earth 13.40M ohms
With all lamps in place sitches closed etc. so trying to explain that this is technically satisfactory. any way they are also saying that it trips of its own accord with nothing turned on. SO i went to the switch plate Feed and neutral are at the switch so from the switch i seperated the circuits and tested out to the centre light (switch wire and neutral then both to earth with lamps removed is between 11 and 13 M ohms) done the same to the wall lights (with lamps removed and just switch wire, neutral and to earth all seperate) same figure. so then tested the neutral and earth of the out going feed to the rest of the small extension same figuer and they have the same style lights fitted throughout. Could this be cheap light fittings?? any advice would be welcome.
I did also explain that using cheap lamps is also a common problem as they dont last but they argued back with that its on the wall lights that do it in that room none of the others go?
I have not gone to far into it as Im am getting over the back operation and shouldnt be working anyway and it was a free test just to try and establish if it was something simple or not.
Thanks