Rcbo | on ElectriciansForums
Discuss Rcbo in the Australia area at ElectriciansForums.net
Hi Guys
I know this sounds daft but could anyone tell me how to wire up a RCBO please, not 100% especially regarding functioning earth.
Many Thanks
Steve
Put your live and neutral in to the RCBO and then the neutral that is attached to the RCBO as a curl pig tail cut that to required size and attach to neutral bar as you would have the neutral that has now gone directly into the RCBO and then the functional earth into the earth bar along with your earth from the circuit.
I am not saying this in a position of full confidence but think its right and therefore would like to be corrected if wrong.
Cheers.
Cheers.
What about any existing residual current devices??:confused:
Surely the neutral and live must be supplied from a point just after the main switch?
? not sure what you mean.
RCBO connects to busbar just like MCBs and the neutral and live from the circuit go into the RCBO.
The main switch only comes into is as that is making the busbar live which the RCBO will be connected to???.
But maybe I have misunderstood what you are asking.
RCBO before the rcd protected circuits and on a different neutral/bus bar as in a high integrety board, causes all sorts of imbalance otherwise!
We are putting high integrety boards into the two houses you and I are doing at the moment......Have a good snout on Monday, Cambridge has 2 RCBOs, 1 for the fire alarms and 1 for the emergency lights, Bury has 1 rcbo for the smokes.
The one I am doing this weekend is an all RCBO board, and at the risk of sounding ---- it looks really smart!!!!
So what if you have a split load board and both sides protected by RCD the RCBO's will cause imbalance? hmmm.
Or you don't need to use an RCBO on a RCD protected CU as its already got that protection.
Reply to Rcbo in the Australia area at ElectriciansForums.net
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Elkay 2235A-1 Energysense White 3 Wire Touch Timer 16A 240V. This is a touch timer (you don't need that bit) which also can be activated by a...