OP
dkent5
The insulation resistance test is for the cables only and not the equipment. The RCBO should also be marked down on your results sheet as equipment vulnerable to tests. For test purposes all the cables to this RCBO would be disconnected. The tests would then be carried out on the circuits protected by the RCBO and would not be a safety issue as the supply should be isolated to perform such tests. Hope this has been some help.