The insulation resistance test is for the cables only and not the equipment. The RCBO should also be marked down on your results sheet as equipment vulnerable to tests. For test purposes all the cables to this RCBO would be disconnected. The tests would then be carried out on the circuits protected by the RCBO and would not be a safety issue as the supply should be isolated to perform such tests. Hope this has been some help.
 
Hi,

Once again...I might be wrong but -

I thought IR testing was to test for leakage - bit like pressure testing a pipe!!

If you disconnect all circuits before IR testing them and then connect them back up (after your

sattisfactory readings) then there is a chance that you may accidently short circuit something when re-

terminating the circuits.

I think this is why we are told to terminate everything before IR testing.

If an rcbo is going to be a problem whilst testing you can:

a) Test at 250 v

b) Replace with an mcb for testing purposes

But....as I posted before- this should only be a problem if the rcbo is part of the circuit that you are

testing.

If you are doing individual circuit IR testing at the CU then you are testing on the outgoing side of the

MCB/RCBO with all switches off so I don't think this will cause any damage.

Disconnecting all the circuits kind of defeats the object of IR testing - IMHO


Wayne,


Wayne
 
Hi Jason,


What would be the answer then if you're IR testing a board full of RCBOs - disconnect their neutrals for

the tests? - or would you disconnect circuits altogether, like some have suggested?

Cheers,

Wayne
 
hi mate, listen to lockhes, i always disconnect the earth & neutral from the rcbo before ir tests. when they ask you to test 3 rcbo's & do ir tests do they mean test trip times on those circuits both the mechanical & with the meter, i would be careful meggering rcbo's for 1 theres a coil in the rcbo even doing tests at 250v gives dodgy readings (gives you the impression there is an insulation breakdown on the circuit) 2 there is an above average chance of killing the rcbo. some rco's even say on the side to disconnect before insulation resistance tests. hope this helps.
 

Reply to RCBOs (INSULATION RESISTANCE TEST) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
935
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
367
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
370

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top