R

Rikki Barrett

Was wondering if there are any types of circuits that could be sensitive to RCBO's???
I need to put an RCBO on a circuit with lots of computers and the like on it, the last thing I want to happen is a nuisance. These computers have to be running and can only lose power once really.

Also can you get different types e.g B,C??

Thanks for any input. Rik
 
Bear in mind that a typical PC has a MA leakage of about 3mA so 10 PC or Less may trip your RCD!!

Type B & C dont worry to much about them..! lots of Manufactures only make Type C RCBO
 
Was wondering if there are any types of circuits that could be sensitive to RCBO's???
I need to put an RCBO on a circuit with lots of computers and the like on it, the last thing I want to happen is a nuisance. These computers have to be running and can only lose power once really.

Also can you get different types e.g B,C??

Thanks for any input. Rik

May i ask why you need to install RCBO to the circuit?
 
The customer has had a PIR done and it has come back with no RCD protection on circuits supplied by t & e, they put there quote in for fuseboard upgrade from 8-way to 12-way TP & N with the 9 circuits on RCBO's.
 
The customer has had a PIR done and it has come back with no RCD protection on circuits supplied by t & e, they put there quote in for fuseboard upgrade from 8-way to 12-way TP & N with the 9 circuits on RCBO's.


There is no requirement to install an RCBO on existing T&E circuits or socket outlets as this is only a code 4 on a PIR.
 
Code 2 according to this guy. And I dont have any insurance in place to dispute that, besides, customer will say ''if thats what needs doing, do it''. I know it.
 
i have a job coming up with 24 workstations- i'm going with 4 workstations per rcbo

i think i'm right in saying they should be the ' A' type

anything critical would prob go through a UPS (assuming you require rcd) i assume that will provide a level of protection against nuisance?
 
Last edited by a moderator:
I regularly put up to about 15 PCs on a single RCBO, depending on the age of the machines and have never had a tripping problem. Strip the sheath off a kettle lead and get your clamp round the earth with one of their PCs running and see what leakage it measures. New systems with flat screens and efficient power supplies don't leak anywhere near as much from what I've seen. One RCBO for each 4 computers just seems like a massive waste of money to me. Plus it would mean some sections of dado trunking in an IT suite having 16 lengths of 2.5 running through it!!!
 
i'd prob get away with 8 easily


what's the 'demand' with those 15 pc's- about 4.5 kw at 300w each?

there'd be no diversity in a classroom situation
 
i'd prob get away with 8 easily


what's the 'demand' with those 15 pc's- about 4.5 kw at 300w each?

there'd be no diversity in a classroom situation

Standard PCs as you've said so 20A, would be on a 32A ring. I wouldn't normally put 15 standard PCs on one ring, have done it with thin clients in the past (around 150W each).
 

Reply to RCBO's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
    • Like
2
Replies
22
Views
2K
  • Question
Ye smaller board (containing the RCBO'S) will literally be next to the MEMSHIELD, And hence the 32A MCB be simply feeding power to a 32A RCBO I...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top