2 radials instead of 1 ring -would be same no. of cables
but less nuisance risk

I suppose that would mean you could have twice as many circuits convering the same number of PCs so as you say, less chance of nuisance tripping as more RCBOs to share the leakage across. It would also mean you had no high integrity earthing in place though which is a requirement for any final circuit with a CPC current exceeding 10mA.
 
interesting-dunno if that applies here in ROI -will check though

is a radial in steel conduit with separate cpc classified as high-integrity earthing? (steel conduit is a parallel fault path)
 
Last edited by a moderator:
interesting-dunno if that applies here in ROI -will check though

is a radial in steel conduit with separate cpc classified as high-integrity earthing? (steel conduit is a parallel fault path)

It's there in the BRB and onsite guide gives a detailed page on it if you work to the 17th still over there? Steel conduit as a separate CPC would be fine, as would running the CPC in a ring using an extra single core and terminating them both under their own screw.
 
Why exactly do you need to fit an RCBO to the computer circuit ? Are you doing it becuse they are 13a sockets or becuase cables are buried or some other reason?
 
check the small red book on circuits that dont require an RCD
if its surface or visible wiring then no RCD is required, ie dado trunking or surface trunking, cables in void above suspended ceiling, you may think EVERY circuit requires an RCD but it doesnt,
check the rules and its your call at the end of the day mate
if its surface and computers I would always fit an MCB
 
Last edited by a moderator:
and as en example of this , when i did my NICEIC assesment, one of the jobs was a circuit totally clipped direct just doing lighting
I installed it on the non RCD side of the split board after checking the rules

the NIC guy didnt even bat an eyelid
 
also in general Commercial permisis dont require RCDS if they are under the supervision ie if theres a building manager,who permits work /doesnt permit work and has an understanding of the regs re cable runs ect
 
check the small red book on circuits that dont require an RCD
if its surface or visible wiring then no RCD is required, ie dado trunking or surface trunking, cables in void above suspended ceiling, you may think EVERY circuit requires an RCD but it doesnt,
check the rules and its your call at the end of the day mate
if its surface and computers I would always fit an MCB


If the person plugging equipment in isnt suitably trained or comptent then u do need rcbo/rcd.
 

Reply to RCBO's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
    • Like
2
Replies
22
Views
2K
  • Question
Ye smaller board (containing the RCBO'S) will literally be next to the MEMSHIELD, And hence the 32A MCB be simply feeding power to a 32A RCBO I...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top