RCBO's | on ElectriciansForums
Discuss RCBO's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Archie
North Norfolk
I have a question,
When testing a circuit protected by an RCBO, lets say a type B, in the max permissible column do you put the value from the Regs for the breaker type or 1666 Ohms?
Rang the NIC Tech line and NAPIT's and they both say different.
It's just that if you put the value from the Regs and there is a high Zs it looks odd on the paperwork.
Cheers
Reply to RCBO's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
7K
suffolkspark
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.