RCCB tripping but no MCBs have tripped. | Page 2 | on ElectriciansForums

Discuss RCCB tripping but no MCBs have tripped. in the UK Electrical Forum area at ElectriciansForums.net

RDB85

-
Trainee
Joined
Nov 23, 2017
Messages
1,085
Reaction score
176
Location
Liverpool
I’ve a Square D Split load RCCB board that has a strange issue. The RCCB trips and none of the MCBs seem to trip.

The only thing that has recently been done is replacing the sockets and switches. I’ve tested each socket with a socket tester and it was showing as correct on all sockets. I only had to extend two which I brought up in a a previous thread and used some 5 way Wago connectors.

Any ideas what it could be? As none of the MCBs have tripped. It only seems to happen of a night.
 
Hopefully it is something simple. I do always check my cables. Maybe Ive missed something:

Ive seen these two Meggers:

Megger Mft1721 Multifunction Tester | 020200158531 | Cash Converters - https://www.cashconverters.co.uk/shop/tools-motor--hardware/power-tools--industrial/multimeters--electrical-testers/multimeter/020200158531


Metrel:

 
As an eBay Associate we earn from qualifying purchases.
The KT64 does seem okay for the price the KT65 is £650 to buy but it’s currently on an Auction for a week. It would probably get close to that. I unsure what to do.
 

Attachments

  • [ElectriciansForums.net] RCCB tripping but no MCBs have tripped.
    FD206F8E-380E-4072-BDE3-405229CDC8B0.png
    1.9 MB · Views: 32
Last edited:

Reply to RCCB tripping but no MCBs have tripped. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
692
davesparks
D
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top