Hello all I am new to this forum. I have a customer who has an office in a flat that was originally built as a domestic accomodation. There exists a ccu which has an 80amp RCCD as it's main isolator and mcb's for the circuits. What's happening is that at least once a day, the RCCD will trip and and they say that this normally happens when they switch on the kettle although they also said that it happened the other day when they switched on their lights.
Any thoughts on resolving this issue would be greatly appreciated.
 
mate i had exactly the same thing!! It drove me bananas! Solved very easily though by getting a Earth Leakage Clamp Meter, basically the RCCB in my case was floating around 24mA and then something would turn on and trip it, they would say its the kettle the fridge the light the dog barking! But basically in my case the underfloor heating was leaking 20mA must have been damaged somewhere along the line so could rip there floors up just had to re jig the breakers!
Seriously though clamp meter is so worth the money on these kind of faults!
 
mate i had exactly the same thing!! It drove me bananas! Solved very easily though by getting a Earth Leakage Clamp Meter, basically the RCCB in my case was floating around 24mA and then something would turn on and trip it, they would say its the kettle the fridge the light the dog barking! But basically in my case the underfloor heating was leaking 20mA must have been damaged somewhere along the line so could rip there floors up just had to re jig the breakers!
Seriously though clamp meter is so worth the money on these kind of faults!

Can you recommend me one as i recon i could hve saved myself at least two days work over the year messing around tracing tripping RCDs - thx
 
Thanks for your reply.
What exactly do you mean by "re jig the breakers".
Thanks.


mate i had exactly the same thing!! It drove me bananas! Solved very easily though by getting a Earth Leakage Clamp Meter, basically the RCCB in my case was floating around 24mA and then something would turn on and trip it, they would say its the kettle the fridge the light the dog barking! But basically in my case the underfloor heating was leaking 20mA must have been damaged somewhere along the line so could rip there floors up just had to re jig the breakers!
Seriously though clamp meter is so worth the money on these kind of faults!
 
Thanks for your reply.
What exactly do you mean by "re jig the breakers".
Thanks.

On a split load board, with two RCDs, you can move circuits from one RCD to the other (physical constraints re cable lengths allowing) to balance out the 'normal leakage'. For example, if the underfloor heating, cooker and kitchen sockets were on the same RCD, then move one or two of them to the other RCD which perhaps is coping with less 'normal leakage'

(I'm sure there is a better phrase than 'normal leakage' but cannot think what it is)
 
The last "RCD" case i did was basically a very large house with absolutely loads of electrical / electronic equipment, much of it would be leaking to earth, as part of its design. The house just had one RCD at 30mA, rather than change the CU, i managed to modify it slightly and get 4 RCBOs in there effectively giving the house 4 times the capacity for natural leakage. The owner just wanted it sorting so i perhaps over clubbed it a bit. Anyway been done for 4 months now and not a peep.
 

Reply to RCCD Tripping at least once a day in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top