futuresparkie

Hello all I am new to this forum. I have a customer who has an office in a flat that was originally built as a domestic accomodation. There exists a ccu which has an 80amp RCCD as it's main isolator and mcb's for the circuits. What's happening is that at least once a day, the RCCD will trip and and they say that this normally happens when they switch on the kettle although they also said that it happened the other day when they switched on their lights.
Any thoughts on resolving this issue would be greatly appreciated.
 
mate i had exactly the same thing!! It drove me bananas! Solved very easily though by getting a Earth Leakage Clamp Meter, basically the RCCB in my case was floating around 24mA and then something would turn on and trip it, they would say its the kettle the fridge the light the dog barking! But basically in my case the underfloor heating was leaking 20mA must have been damaged somewhere along the line so could rip there floors up just had to re jig the breakers!
Seriously though clamp meter is so worth the money on these kind of faults!
 
mate i had exactly the same thing!! It drove me bananas! Solved very easily though by getting a Earth Leakage Clamp Meter, basically the RCCB in my case was floating around 24mA and then something would turn on and trip it, they would say its the kettle the fridge the light the dog barking! But basically in my case the underfloor heating was leaking 20mA must have been damaged somewhere along the line so could rip there floors up just had to re jig the breakers!
Seriously though clamp meter is so worth the money on these kind of faults!

Can you recommend me one as i recon i could hve saved myself at least two days work over the year messing around tracing tripping RCDs - thx
 
Thanks for your reply.
What exactly do you mean by "re jig the breakers".
Thanks.


mate i had exactly the same thing!! It drove me bananas! Solved very easily though by getting a Earth Leakage Clamp Meter, basically the RCCB in my case was floating around 24mA and then something would turn on and trip it, they would say its the kettle the fridge the light the dog barking! But basically in my case the underfloor heating was leaking 20mA must have been damaged somewhere along the line so could rip there floors up just had to re jig the breakers!
Seriously though clamp meter is so worth the money on these kind of faults!
 
Thanks for your reply.
What exactly do you mean by "re jig the breakers".
Thanks.

On a split load board, with two RCDs, you can move circuits from one RCD to the other (physical constraints re cable lengths allowing) to balance out the 'normal leakage'. For example, if the underfloor heating, cooker and kitchen sockets were on the same RCD, then move one or two of them to the other RCD which perhaps is coping with less 'normal leakage'

(I'm sure there is a better phrase than 'normal leakage' but cannot think what it is)
 
an even better way would be to supply the UFH from it's own RCBO. that's the beauty of hi-integrity CUs.
 
The last "RCD" case i did was basically a very large house with absolutely loads of electrical / electronic equipment, much of it would be leaking to earth, as part of its design. The house just had one RCD at 30mA, rather than change the CU, i managed to modify it slightly and get 4 RCBOs in there effectively giving the house 4 times the capacity for natural leakage. The owner just wanted it sorting so i perhaps over clubbed it a bit. Anyway been done for 4 months now and not a peep.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCCD Tripping at least once a day
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
futuresparkie,
Last reply from
plugsandsparks,
Replies
8
Views
1,530

Advert

Back
Top