Dec 6, 2017
Messages
26
Reaction score
0
Location
Portsmouth
So had to fit a new shower as old one kept tripping the rcd after few seconds assumed the shower was to fault as made a buzzing noise and tripped, on fitting the new shower it had same faukt so checked pressure of water no issue then checked wiring at box also no issue so moved onto next possibiliy of short on cable.
Yes maybe should of used multimeter and tested each one out but easier as short run in walls so run new cable exactly the same.
So decided to wire a small flex with bulb holder on that trips rcd changed the 40amp mcb to a 16 amp tried light also trips could this be a faulty rcd its rated 80amp 30ma, we also tested the the curcuit with every mcb turned off with only shower circuit on and also tripped.

Any help would be greatly appreciated as would like to think in a 6 bedroom house with each room occupied that of rcd was faulty then it would trip as currently has approx 8 circuits on and only randomly started to happen nothing new has been added.

[ElectriciansForums.net] Rcd advice needed faulty or fault
 
Problem is now fixed the live off 32amp mcb was obviously causing the circuit to trip as resistance check wasn' connecting thanks to everyone who has helped and I tested n-e with multi meter with no shorts anywhere so rechrckef lives to find one had snapped
A high resistance connection will not cause an RCD to trip and a multimeter will not output sufficient voltage to show up most faults.
Good luck with your continuing electrical career.
 
thanks to the people that helped and inwomt be returning here as people are not overall friendly.
I've found people on here to be very friendly and helpful. However, when you repeatedly ignore the advice given because it's not what you wanted to hear, everyone gets frustrated and you will get some stick.
 
A high resistance connection will not cause an RCD to trip and a multimeter will not output sufficient voltage to show up most faults.
Good luck with your continuing electrical career.
Well it's fixed I redone earths as Well as I think 1 had come out and exterminated all the neutrals I was going to tidy box up but left as it was as it was signed off like it before.

Things are all connected correctly it's not like ive added it to a non protected rcd circuit so a loose connection could have been there asWell, i haven't dangerously bypassed anything or added to a non rcd side like some cowboys would do it's all connected as should be and not tripping.

Also like I said yesterday when wired to a light bulb it also tripped so wasn't tripping under load even with shower was the same after doing fuse box today tested with light bulb and didn't trip fault is fixed not bodged or covered up.
 
Last edited:
Well it's fixed I redone earths as Well as I think 1 had come out and exterminated all the neutrals I was going to tidy box up but left as it was as it was signed off like it before.

Things are all connected correctly it's not like ive added it to a non protected rcd circuit so a loose connection could have been there asWell, i haven't dangerously bypassed anything or added to a non rcd side like some cowboys would do it's all connected as should be and not tripping.

Also like I said yesterday when wired to a light bulb it also tripped so wasn't tripping under load even with shower was the same after doing fuse box today tested with light bulb and didn't trip fault is fixed not bodged or covered up.

Are you a dalek?
 
Are you a dalek?
Lmfao meant to say re-terminated that' Samsung auto correct for you and the fuse box is also being changed soon in the house as it's a plastic one.
Due to current regs with the 3 yearly check I am aware that being under the stairs that they now have to be metal and non combustible with current regs.

Will have to post a pic of my consumer unit in the property I rent you will all comment on that
 
Are you a dalek?
Its not the neutral he will be exterminating if it all goes wrong, it will be the poor sod in the shower or house when it goes kaput who will exterminated.... its okay though they might find his fingerprints all over the CU so guilty as charged your honour. I don't think he will be able to use the competent person defence!
 
This has gotta be a wind up by admin surely. 3yr checks, needing to change board, broken ring and the 16A light cct.... It's not making much sense at all. I'm not gonna bite again after this message.
 
Its not the neutral he will be exterminating if it all goes wrong, it will be the poor sod in the shower or house when it goes kaput who will exterminated.... its okay though they might find his fingerprints all over the CU so guilty as charged your honour. I don't think he will be able to use the competent person defence!
No finger prints as I wore my marigolds
 
Lmfao meant to say re-terminated that' Samsung auto correct for you and the fuse box is also being changed soon in the house as it's a plastic one.
Due to current regs with the 3 yearly check I am aware that being under the stairs that they now have to be metal and non combustible with current regs.

Will have to post a pic of my consumer unit in the property I rent you will all comment on that

what 3 year check?

Who says that they have to be metal?
 

Reply to Rcd advice needed faulty or fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
870

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top