RCD and replacement fails to operate | Page 3 | on ElectriciansForums

Discuss RCD and replacement fails to operate in the UK Electrical Forum area at ElectriciansForums.net

Joined
Apr 24, 2017
Messages
6
Reaction score
2
Location
Sussex
On completion of some recent minor work , I carried out the usual testing and noticed the incoming 100A 30mA rcd on the Consumer unit was failing to trip at X1 and X5 at both 0 & 180 degrees Further investigation revealed that the test button on the device failed to trip it as well . All well and good so far faulty RCD me thinks . How often do these devices actually get tested by the end user (despite the quarterly test label ) Replaced it . Checked again and although test button now trips, it still fails to pass RCD ramp or time tests ? Just in case the replacement unit was faulty ( however unlikely ) , I had another unit on the van changed that out with the same result .
Earth loop impedance testing on both on the ring final and incoming Ze, very low reading less than 1 Ohm bearing in mind this is a TT installation ( does seem exceptionally low,) I have checked all round the incoming supply head no sign any PME link I may have missed ????

Any ideas fellow sparks
 
Yeah I learnt that the hard way too, in a hurry to get out of a pub (!) before they opened - did the live RCD testing without fully unplugging everything - found the trip times were really slow - way past the limits, so I thought I should change it. Came next day with a new RCBO. When I powered everything down and removed the outgoing conductors I thought "I'll just do one more test before I remove it..." and it tested spot on. That was a Merlin RCBO, and the cause was a fridge. I've seen the same effect a few times and it only seems to be things with motors that cause it ???
 
I had a similar problem on a TT a few years back due to a N-E fault. I can't remember the details but I'm sure it was a single split load board with a main switch & a standalone 100mA RCD. The fault was on the non-RCD side of the board which added to the confusion. Once I'd located the faulty circuit I left the neutral disconnected & then retested the RCD & hey presto.......!
This may not be the issue here but it sounds very familiar to the one I had, hope this helps if you haven't already sorted it.
 

Reply to RCD and replacement fails to operate in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
It can also mean lasts or continues for two years.
Replies
14
Views
1K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top