OP
As @newfutile has just said, you would need a very peculiar fault to allow a typical SELV supply to be driving N-E and not go bang! very shortly after.
Anyway for the purpose of the original discussion, that would a 30mA B-type RCD allow enough current to upset a 100mA incomer, the answer is very definitely no. Certainly so if the earth rod Ra will allow for much more than 100mA to flow as you are interested in hard-fault disconnection, not shock protection as such.
However, what is also clear is for 30mA shock protection you can't allow more than a 100mA or so of DC to be present so if the EV charger or PV inverter says 'type B' is needed, then it matters.
Anyway for the purpose of the original discussion, that would a 30mA B-type RCD allow enough current to upset a 100mA incomer, the answer is very definitely no. Certainly so if the earth rod Ra will allow for much more than 100mA to flow as you are interested in hard-fault disconnection, not shock protection as such.
However, what is also clear is for 30mA shock protection you can't allow more than a 100mA or so of DC to be present so if the EV charger or PV inverter says 'type B' is needed, then it matters.