Greg:
I have been away from a refurb job while other (inc. the owner) have been in and on my return I found that the RCD (for a cooker circuit and three power circuits) is tripping. It triped even when a fairly basic piece of equipment such as my makita drill charger of the owners kettle was plugged in. Thankfully my kettle was fine. It tripped when items were put onto each of the 4 circuits with the other circuits switched off. I put in a new RCD and the same happened.
Then, at least for me, it gets stranger. I did an RCD auto test on the new RCD in connection with the 4 circuits mentioned and it refused to trip. I consistently got a reading of >30mA and I was perplexed and began to question my tester. I went out of the premises, knocked on some neighbours doors and presented a request which roughly said "this may sound strange but it would really help me if I could test your electrical equipment". With good grace someone let me and my tester tripped the RCD in an expected fashion.
I took the new RCD out and wired it in as an external item to the board. sequence of equipment was Main switch> breaker> RCD> socket> tester and the results that I got for my auto test were 34ms, 34ms, 24ms and 10.9ms.
I did some brief IR tests (I was expect elsewhere and missed NE on three of the circuits) and got results typically in the 300 Mohm range. Ze measured 0.25 ohms.
Nothing was plugged in while tests were conducted and the isolator for the boiler was switched off.
This whole thing doesnt make any sense to me and advice would be appreciated.
Then, at least for me, it gets stranger. I did an RCD auto test on the new RCD in connection with the 4 circuits mentioned and it refused to trip. I consistently got a reading of >30mA and I was perplexed and began to question my tester. I went out of the premises, knocked on some neighbours doors and presented a request which roughly said "this may sound strange but it would really help me if I could test your electrical equipment". With good grace someone let me and my tester tripped the RCD in an expected fashion.
I took the new RCD out and wired it in as an external item to the board. sequence of equipment was Main switch> breaker> RCD> socket> tester and the results that I got for my auto test were 34ms, 34ms, 24ms and 10.9ms.
I did some brief IR tests (I was expect elsewhere and missed NE on three of the circuits) and got results typically in the 300 Mohm range. Ze measured 0.25 ohms.
Nothing was plugged in while tests were conducted and the isolator for the boiler was switched off.
This whole thing doesnt make any sense to me and advice would be appreciated.