Comments welcome please :rolleyes2:

rcd trips once or twice a day been doing so for a couple of weeks
often trips during the night or when occupants are out


wylex 30 mA
serves four circuits
two rings
one radial socket
cooker

fairly new install 15 years
board updated 4 years ago during spruce up

ramp tested trips at 8 mA when tested at sockets in kitchen
19 mA when tested at board
cant test on up stairs sockets as they are all L-N reversal ! ( occupant admits to changing all the sockets for metal ones) will fix that tomorrow



why does the ramp test vary between test at sockets and test at board ?
( changed rcd and new one does the same)


would L-N reversal on adjacent circuit affect the rcd this way? seems it might
 
The Cables were not isolated at the CU, so if it is a cable or JB or accessory that is breaking down, it would still allow enough leakage to affect your readings.

Don't forget that MCB's are single pole (in the UK at least) and don't in general isolate the N.

have some more time tomorrow to investigate , just did nt think the conductor insulation would have any bearing if not under load, thanks for the replies..
 

Reply to RCD Conundrum in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
860
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
657

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top