RCD dates | Page 2 | on ElectriciansForums
Discuss RCD dates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As Imhave said previously its your report, so you code it as you see fit. Just make sure your PI insurance is upto date though.
But given its retrospective, if it didn't need one at time of installation then surely it's a c3?
It's completely irrelevant whether or not it complied when it was installed. You are assessing the installation against the current standard (BS 7671:2008 (2013)) and the notes attached to the model forms in the Wiring Regulations state that any lack of an RCD for additional protection must be given a minimum of a C3 classification.
So you need to assess how great the risk is.
Of course, the "easiest" way to avoid a code 2 is to change a couple of sockets front & back for rcd protected ones, or protect the ground ring with an rcbo.
Reply to RCD dates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.