T

Templer

Hi I have a 6 way split load board located in the shed and served by 10mm SWA. Anything on the unprotected side of the board tests and works fine. However this is not the same for the protected side. I can plug a radio in and the circuit does not trip, but if I use the lawn mower or a drill the RCD trips immediately. In addition, the RCD does not trip when the test button is pushed. I have swapped out the RCD too. Nothing trips on the house board when the RCD in shed trips. All connections are secure in CU. Any ideas where to go next?
 
If the RCD is wired correctly plus there's power to it and it doesn't trip on the test button then replace it again, no if's or but's, it's faulty. The tripping under load could be a crossed/borrowed neutral or an insulation fault or it could also be a symptom of a faulty RCD.

Replace it then do global IR testing and recheck neutrals.
 
I have had this happen with the neutrals being crossed over to a different neutral bar. Id check that first and also treble check the wiring on all protected circuits but as Marvo says, if its wired correctly and the trip button doesnt activate then the RCD is faulty...
 
Hi Jabbajaws. I have removed all circuits from the board and fitted a single socket and it still trips. I will check the neutrals. Would crossed neutrals cause the RCD not to trip on test?
 
Hi Jabbajaws. I have removed all circuits from the board and fitted a single socket and it still trips. I will check the neutrals. Would crossed neutrals cause the RCD not to trip on test?
One Neutral should come from the bottom of the Main switch into the first neutral bar, then from that neutral bar into the top of the RCD, then from the bottom of the RCD into the second neutral bar.
 

Reply to RCD doesnt trip on test. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
858

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top