Hi I have a 6 way split load board located in the shed and served by 10mm SWA. Anything on the unprotected side of the board tests and works fine. However this is not the same for the protected side. I can plug a radio in and the circuit does not trip, but if I use the lawn mower or a drill the RCD trips immediately. In addition, the RCD does not trip when the test button is pushed. I have swapped out the RCD too. Nothing trips on the house board when the RCD in shed trips. All connections are secure in CU. Any ideas where to go next?
 
Check inside the garage board. I had a fault exactly the same as this last week. RCD would hold but wouldn't work on the test button. Tripped on Zs test.Wouldn,t trip on any RCD tests. Disconnected everything from RCD and it worked perfect. Tripped on test button and all trip times within limits. As soon as busbar and outgoing neutral reconnected fault re appeared. Turned out to be an earth nicked on neutral bar. Once that was sorted all was perfect. Not saying this is definitely your problem but worth a look.
 
Check inside the garage board. I had a fault exactly the same as this last week. RCD would hold but wouldn't work on the test button. Tripped on Zs test.Wouldn,t trip on any RCD tests. Disconnected everything from RCD and it worked perfect. Tripped on test button and all trip times within limits. As soon as busbar and outgoing neutral reconnected fault re appeared. Turned out to be an earth nicked on neutral bar. Once that was sorted all was perfect. Not saying this is definitely your problem but worth a look.
I am tempted to put in another board. This one is an Excel, but I don't want to do all that and the fault still exists. There are benefits to buying a property that has unfinished work, but there are also many issues!
 
Board change could be and probably is pointless.

The test button on the RCD is purely to make sure the RCD is working properly, it's nothing to do with the installation. If it doesn't trip when you press the test button then replace it, if you put in another and it does the same replace it again - they are dodgey RCD's. What make is the RCD? (sorry if already mentioned, just cba to read the full thread) stick a hager RCD in, more money but you get what you pay for and that is quality.

Replace RCD for a fully functioning one, then global IR to see if there are any issues with the installation. Board change probably unnecessary.
 
Board change could be and probably is pointless.

The test button on the RCD is purely to make sure the RCD is working properly, it's nothing to do with the installation. If it doesn't trip when you press the test button then replace it, if you put in another and it does the same replace it again - they are dodgey RCD's. What make is the RCD? (sorry if already mentioned, just cba to read the full thread) stick a hager RCD in, more money but you get what you pay for and that is quality.

Replace RCD for a fully functioning one, then global IR to see if there are any issues with the installation. Board change probably unnecessary.
Hi Mark, thanks for the reply. The RCD is the same as board, Excel.
 
If you've bought a replacement Excel RCD and it doesn't trip when you press the T button, send it back.

When im doing installations, unless the client is on a poor budget i always fit either hager or Mk - there is a reason why some RCD's are 10x the price of others, even though they do the exact same thing lol.
 
If you've bought a replacement Excel RCD and it doesn't trip when you press the T button, send it back.

When im doing installations, unless the client is on a poor budget i always fit either hager or Mk - there is a reason why some RCD's are 10x the price of others, even though they do the exact same thing lol.
Will a hager or MK fit into an Excel board?
 
Templar - have a think about what happens when you press that test button.

I suspect you have a N-E fault. Your radio probably doesn't even draw 30mA so wouldn't trip it anyway.

Try testing the T button on the RCD with ALL the MCBs tripped and circuit neutrals disconnected - I bet it works.


If you have a short N-E in one of the circuits this board supplies, the test current generated when you press the button will be divided through the actual fault path, and also the artificial one provided by the test button. The odds are that the device will not trip because the required trip current will not met.

Worth trying.....
 
Templar - have a think about what happens when you press that test button.

I suspect you have a N-E fault. Your radio probably doesn't even draw 30mA so wouldn't trip it anyway.

Try testing the T button on the RCD with ALL the MCBs tripped - I bet it works.


If you have a short N-E in one of the circuits this board supplies, the test current generated when you press the button will be divided through the actual fault path, and also the artificial one provided by the test button. The odds are that the device will not trip because the required trip current will not met.

Worth trying.....
Interesting... I have removed all circuits from the board and it still does not trip on test.
 
Sorry buddy, I edited the post after I read it through again, did you disconnect final circuit neutrals too?
Hi board has no circuits on it apart from a single socket on a lead and the RCD does not trip on test but trips as soon as load is placed on it. Could I have a N-E fault on the SWA? If so, would it not trip the RCD in the house CU which feeds it?
 
Hmmmmnnnn

See, if you also have the RCD in the main board supplying, you are still dividing the test current between two RCDs. It's a difficult one.

You really need to be able to IR test.

Do you have an unprotected way on the main board to connect the external board to?
 

Reply to RCD doesnt trip on test. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
858

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top