Hi, I've been installing a new shower, using a shower consumer unit complete with rcd. All the tests passed, r1 And r2 were 0.23 ohms, insulation resistance was >299M ohms, polarity was correct. But when I test the rcd I cannot get it to trip. It passes when the test button is pressed but will not pass the rcd test at 1 or 5 times, it fails to trip and my tester says time exceeded and shuts off.
Every thing appears correct I ran out of time so have isolated it the shower and will investigate it again tomorrow.

all advice would be appreciated.

thanks
 
Onions, thanks for that, that was what I was thinking, i was beginning to think I had missed something. But as the r1 and r2 and insulation tests are ok there shouldn't be a damage to the cable. I checked all connections were tight in both the shower and the switch unit.

Zs test at shower would have confirmed your earth was good without the rechecking of all your connections (as you already done r1 & r2)

You said you checked the other RCD with the plug attachment - I would check both RCDs, at the board, with the leads - if one trips and the other doesn't then as Onions said......
 
Hi, I've been installing a new shower, using a shower consumer unit complete with rcd. All the tests passed, r1 And r2 were 0.23 ohms, insulation resistance was >299M ohms, polarity was correct. But when I test the rcd I cannot get it to trip. It passes when the test button is pressed but will not pass the rcd test at 1 or 5 times, it fails to trip and my tester says time exceeded and shuts off.
Every thing appears correct I ran out of time so have isolated it the shower and will investigate it again tomorrow.

all advice would be appreciated.

thanks
You have not mentioned ZS! I take it your shower unit has a ZE /Ra ?
 

Reply to Rcd fails test. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
640

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top