Rcd fault not tripping | Page 2 | on ElectriciansForums

Discuss Rcd fault not tripping in the UK Electrical Forum area at ElectriciansForums.net

no continuity between any circuits with mcb's off, no continuity between neutral bars with rcd's off and no neutral earth / live earth with main switch off until boiler is connected.
Just checking: this was a continuity (low ohms) test? Have you tried an IR test at 250V between the two RCDs? (both RCDs open, all MCBs closed, boiler spur closed, boiler plug connected to boiler. IR test from N and busbar of one RCD to N and busbar of other RCD.)

IR all clear apart from boiler and that reading is 0.00
Have you tried testing this as a continuity test?

I have not done insulation resistance between live and neutral on lights as I haven’t removed all the lamps.
I'd say this is probably unnecessary, it's not something I would bother doing if it was me.
 
Wanting to explain this yet do not know how you are testing so basics:

One reason why a RCD won't trip is a N - E fault that is allowing a small part of the current to flow back along the Neutral. Because of this the RCD does not see the full imbalance that the test is creating.

A small enough resistance that your IR tester won't have the resolution/range to indicate it :
Q. you are showing 0.00 M ohms - Is that correct?
I have assumed you are reading this at the boiler plug.
Q. Same test using the circuit continuity setting on your MFT and a resistance reading that will be greater than the range on your continuity test - perhaps >200 ohms - Is that correct? .

I hinted at this a few posts back. I gave an example figure of 1500 ohms and asked what would this resistance read if measured using your insulation tester.

Q. The boiler once cleared from the system (unplugged) reverts all RCD's to operational. When the boiler is plugged in the RCD will not trip - Is that correct?

A N - E will not be lost isolating the circuit from the rcd by the single pole MCB
A N - E fault in circuit at certain values of current flow can stop an RCD from tripping.

It has been already mentioned to forget the lights for now.

Getting late and delayed coming back to you. Consider what I have said.
I have asked the questions here in this post because I am not clear how you are testing and where your results are being obtained. Hence the N - E situation that could be the issue that I have layed out.
 
Last edited:
One reason why a RCD won't trip is a N - E fault that is allowing a small part of the current to flow back along the Neutral. Because of this the RCD does not see the full imbalance that the test is creating.
It could be a large part of the test current flows back through the neutral, if the N-E fault gives a better path back to the transformer than the earthing arrangement does. This could be the case for a TT earthing arrangement, or a high resistance joint to a TN.

Not only could it cause the RCD to not trip when under test, but it could also explain why RCD1 trips when RCD2 is tested:

The test current from RCD2 would be leaked to the MET, most of it flow up the CPC to the N-E fault, and back through the N of RCD1. Both RCDs see an imbalance.
 
It could be a large part of the test current flows back through the neutral, if the N-E fault gives a better path back to the transformer than the earthing arrangement does. This could be the case for a TT earthing arrangement, or a high resistance joint to a TN.

Not only could it cause the RCD to not trip when under test, but it could also explain why RCD1 trips when RCD2 is tested:

The test current from RCD2 would be leaked to the MET, most of it flow up the CPC to the N-E fault, and back through the N of RCD1. Both RCDs see an imbalance.
Exactly.

I was going to ask on the earthing once he clears this boiler fault (suspect on internal component).
OP mentions oil boiler but makes no comment on bonding to oil feed pipe, only that the water incomer was plastic.
 
Last edited:

Reply to Rcd fault not tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Is this a rcbo consumer unit ?
Replies
2
Views
283
Follow the eic test result page .start with ring continuity including figure of 8.then choose between phase and earth connected together on al...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top