I have a customer with a single rcd board, protecting the sockets and the garage only. They wanted a fan installing in the bathroom which needs to be rcd protected. I was going to pit and RCBO on the board for the upstairs light but crabtree have discontinued them. So I though I would install a RCD Fused spur.

I split the bathroom lighting circuit in the rose and did the following.

Ran a L N SL from the rose to the rcd using 3 core
Connected L N to rcd and SL to fan isolator switch
Connected L N from RCD to fan isolator
Connected bathroom light switch to L SL of isolator
Connected L N SL to fan

Basically what happens is the rcd unit trips out as soon as I turn the bathroom light switch on. If I remove the neutral from the rcd direct to the fan isolator everything works fine, but obviously the rcd is then useless.

I suspect a neutral issue but all lights have the same neutral. Any ideas?

Thanks In advance
 
i see you logic there , spin, can't disagree with you on that. fair few ifs though. wonder what malcolm's thoughts are on this one.
 
Fault protection and additional protection should never be required whith a sound and fault free installation.
However faults do occur, vermin eat cable insulation, vibration causes terminations to loosen, carpet fitters bang nails through cables etc.
It used to be that only certain fixed equipment in bathrooms required RCD protection, now it is all circuits of the bathroom, not the equipment, not part of the circuit or just alittle bit of the circuit in the bathroom.
 
i totally agree with you there. always allow for the unforseen. i've always erred on the side of caution, did a CU job last month. was no RCD whatever. existing buried cable (SWA) been in for donkeys, feeding floodlights on his horse paddock. was concerned if would be problems if this was RCD protected, no, after seeing what happened at newberry, i'm bloody glad i wired it to the RCD.
 
Yes it could very well do so.
Something that should be considered when designing any installation that includes a special location.
I believe the main concern is the availabillity of earth fault paths and the impedance of those paths.
What for instance would be the earth fault path for a fault on the ring feeding the bathroom, if the CPC of the ring was disconnected for whatever reason from the earth bar at the CU?
Would that earth fault path be available for a similar CPC failure for other circuits that are not otherwise connected to the bathroom?

Yes the MCB should trip with just about any fault, so why then are we required to provide RCD protection at all?

Good questions, In a hypothetical situation, where cpc's are disconnected, the earth path would have to be to whatever earthed metal is around, maybe there wouldn't be one, perhaps you are making a case for all circuits to be RCD protected, as they are in other countries, but if the cpc's are disconnected even that wouldn't make a difference.
 
Last edited:
Spins correct, when any fault to earth exists, all extraneous conductive parts connected to the met and exposed conductive parts will see a rise in potential,itsw the duration which is the issue. In the sixteenth, they used to have a reg regarding mixed disconnection times, .4 and 5 secs, where there was a possibility of a 5 sec fault appearing on a circuit which required .4 disconnection, it was dropped i believe due to harmonization.

Hence why one of the conditions along with a rcd for omitting supplementary bonding is by ensuring extraneous conductive parts within the location are effectively connected to the met.
 
Sorry NRG, went off on our own there for a while, forgot about you, the majority opinion seems to be, fit your bathroom RCD, make sure all electrical equipment in the bathroom is supplied through it, and make sure all your cpc's are connected and continuous.
 
Yes my own fault! So basically run my incoming live and neutral to the rcd unit and then back to the ceiling rose and connect as you would normally to Fan Isolator and onto fan.
 
yep that is the only sensible way if providing it can not be achieved at origin, you are only working on the lighting circuit and so that is all you are responsible for, ensure the work you carry out is covered and you have done all you can.
 
Last edited by a moderator:

Reply to Rcd fused spur bathroom Fan in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
194
  • Question
It would normally be the outer terminals where the flex of the pendant drop connect.
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top