A customer has a RCD spur unit spurred off a ring supplying their garage. It is all wired in 2.5mm twin, and in the garage there is only two sockets with nothing plugged in.

The RCD spur unit would not reset so have replaced with an identical one. When the power was turned back on the the spur unit was already on and everything was working fine, but when i tested it via the test button there was a lovely flash and the RCD in the ccu tripped too. And that broke the spur unit.

I have dead tested all the cables and all the readings are perfect.

Is it a problem with the RCD spur units or is there anything else I can check that I have missed?

Thanks
 
not quite i think you'll find the 30 ma would trip before the 100ma so no need for time delayed if you have a fault drawing more than 100ma then both will trip , but think youll find that a 30 ma RCD will trip at around 24ma so way before the 100ma

Disagree, unless you have a fault of less than 50mA it is likely that both will operate, agree with Londonlec the upstream RCD would need to be time delayed.
 

Reply to RCD fused spur unit fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
691

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top