A

andrewcann

hi all just want to check that i am right have been ask to check over another sparks work in a first floor flat all he has done is added 3 new sockets in the kitchen the only thing is it is a old ccu with rewireble fuse and no rcd as the cables are buried in the wall it needs to be on a rcd. one of the new sockets is spured of a old scocket chase in the wall and down down by 600mm and am i right in it still need to be on a rcd just wanted to make sure before i say anythink to the customer
 
Sockets intended for general use and cables buried at less than 50mm should be on an RCD to comply with the current Bs7671....rewirable 3036 fuses are still an acceptable means of overcurrent and fault protection.
Bs 7671 is not statutory though, and it may be that the installer has taken the view that as no other circuits are RCD protected there is no point in providing RCD protection for just 3 additional sockets,the installation will not be any worse than before..and if it is a first floor flat,the sockets are not likely to supply equipment outdoors...I have some sympathy with that view,although not strictly correct.
More importantly has the main bonding and earthing been confirmed as adequate?
 
Last edited by a moderator:
yes all the main bonding ie gas and water is in 10mm its just as it was in a kitchen and comes under special locations and cables are buried needs to be on a rcd think he has put cables in 20mm tube so not sure if thats why its not on a rcd
 
if he adapted an existing circuit and surfaced his cable like you said in tube wouldnt he be exempt from adding an rcd to protect the cables? could be wrong i would recommend it to the customer anyway and make a note of it also
 
ah right didnt see the buried bit so added cable to an existing circuit, but the new cable isnt protected by earthed mechanical protection or 50mm deep in the wall so must have rcd protection or exempt because its minor works??
 
If it was me an to cover my own back i would at least fit an rcd spur for the additional sockets,its not pretty but at least meets the regs,im not sure how the niceic etc would view the practise carried out on this one as in theory it does not meet the regs but as already posted he has made the installation no worse than it was before,and when a client just wants a few extra sockets they dont want to pay for all that extra work and they think we are pulling a fast one,i am quoting for wiring an upstairs extension at present no rcd on sockets,will i be incorporating rcd protection oh yes.
 
As WP stated the electrician most likely assessed by test ie the Zs of the Ring final that the existing installation met the ADS of the BS 3036 Fuses, and omitted the use of RCD protection, also being a first floor flat may have also influenced him/her

Again there is nothing wrong in this if as the designer you feel that is safe to do so........................that is until something went wrong!!

The very start of the Regulations in it's introduction advises us that

"The Regulations apply to the design,erection and verification of all electrical installations, also including additions and alterations to existing installations............."

So by omission of RCD protection for the sockets as per regulation 411.3.3 and for the cable 522.6.6 then it would be unwise to advise the client all is well IMO.
 

Reply to rcd in kitchen in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top