hi could anybody please tell me the following thankyou type of protection afforded by the following rcd's and suggest an application for each 30ma, 200ma and 500ma
thankyou
 
I must admit I have never heard of nor seen a 200mA RCD.

In TT installations the usual course was a 100mA time delayed RCD to provide additonal earth fault protection in conjunction with a 30mA RCD which provides additional protection against the failure of basic protection and fault protection.

300mA RCD's are used primarily in agricultural installations and also for protection against fire.
 
you say 100ma time delay is by the by does this mean its now not required?its just am bout to start a re-wire with a tt supply and am in process of registering with napit and this is a job they will be visiting.
 
you say 100ma time delay is by the by does this mean its now not required?its just am bout to start a re-wire with a tt supply and am in process of registering with napit and this is a job they will be visiting.

If the Installation as a front end 100mA RCD and it is in good working order then there is no need to change it, in fact it gives you a few more options on the type of CU etc you can fit.

If it has a front end ELCB then you will have to remove it, and then go either for a dual rcd board or RCBO's
 
This is a little dated (16th Ed) but it does give you some ideas as to what the different ratings of RCD are used for.

As I said it is a bit dated asa the 17th Ed now requires 30mA RCD to a lot more situations.
 

Reply to Rcd information in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
709
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Hi All, Looking for some advice into my build. What I've basically done is add additional RCD protection to my 100% off-grid 12V 3300W Inverter...
Replies
0
Views
155
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top